7/18/2017 3:40 PM | |
Posts: 59 Rating: (0) |
I am trying to establish communication between s7-1511-1PN and Logo 8 FS4 but not getting success. Can you post your sample program! ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 7/26/2017 7:38:15 AMNew subject after splitting |
7/18/2017 4:40 PM | |
Joined: 12/18/2014 Last visit: 9/19/2024 Posts: 33799 Rating: (4199)
Here is a simple example. In the Ethernet connection, the LOGO! must be configure as a client and the S7 as a Server. AttachmentProject_LOGO!8.FS04.zip (418 Downloads) |
This contribution was helpful to3 thankful Users |
7/18/2017 8:53 PM | |
Sorry, I do not have TIA. Maybe the attached PDF-file will help you on the S7 side. Please ensure that you have to adapt the IP addresses and the TSAPs to your requirements. AttachmentEN_LOGO!-S7-1200_communication.pdf (462 Downloads) |
This contribution was helpful to2 thankful Users |
7/19/2017 6:16 PM | |
Dear Sir, I have established communication between S7 1511-1 PN and Logo 8! FS4. Thanks for your support. |
This contribution was helpful to1 thankful Users |
8/7/2017 10:59 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by fiah is split to a separate thread with the subject Example Project for: HMI tag (editable) and data type ( selectable from 1 to 99). Best regards |