4/6/2022 4:20 PM | |
Joined: 11/5/2019 Last visit: 6/29/2024 Posts: 2 Rating: (0) |
Hello experts. Please help solve my problem. My topology: PLC CPU 1516F-3 PN/DP: 192.168.100.2 ; 255.255.254.0 CP card CP 1543-1:192.168.2.2; 255.255.255.0 PC: 192.168.2.199; 255.255.254.0 Multiuser server 192.168.2.193; 255.255.254.0 The problem arises when I uploading the HW configuration via the multiuser server trough the CP card. In halfway, the dowlanding will stop with an error. And PLC remains in the STOP MODE. Security information: System initiated session termination SessionID 0-16643 Client IP addr: 192.168.2.199 A previosly established system session was terminated due to CPU operating system security efforts. The interesting thing is that the HMI which is on the network of CP cards will display an error about disconnection from network at the moment when I get an error while dowlanding. The reason why I have a multiuser server on the CP card network is the one because I can dowland PLC and HMI from this network. if I have it connected to the PLC network, I can only download the PLC and not the HMI. Thank you for your help. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 04/07/2022 09:12:10New subject after splitting. Text edited for better reading. |
|
4/12/2022 9:33 AM | |
Joined: 8/3/2009 Last visit: 10/15/2024 Posts: 13952 Rating: (1759) |
Hello tomas234 you should be able to use downloading the HMI with S7 routing also from PLC network: https://support.industry.siemens.com/cs/ww/en/view/90528617 Bye Murof |
If this Information really helps, you could use the Rate function |
|