Dear Ing.Hass, You are mentioning a Ethernet CP (CP343-1), with this module you can not use Modbus RTU When you want to use Modbus RTU, you need a serial CP, like CP341. This CP is possible in three variants. One example is RS485, (6ES7 341-1Ch01-0AE0) Then you also need a Loadable driver for CP341, so it can act as Modbus RTU master or Modbus RTU slave. Here are some manuals: SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs:Modbus protocol, RTU format, S7 is Master SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs:Modbus protocol, RTU format, S7 is Slave Best regards, Wizard |
This contribution was helpful to2 thankful Users |
8/10/2010 6:53 PM | |
Joined: 1/17/2007 Last visit: 7/29/2024 Posts: 1544 Rating: (534)
|
Another option would be to use modbus TCP via your CP343 using the Open Modbus TCP software from IT4Industry, and then use a TCP / RTU convertor. Lantronix do a very good one called XPress-DR-IAP. I have used these in the past and they are very good indeed. This acts a TCP modbus slave and a RTU modbus master, so it will be a gateway between the TCP master that is your CP343 and the RTU slave that you want to interface to. |
Programming today is the race between software engineers building bigger and better idiot proof programs, and the universe producing bigger and better idiots. |
|
This contribution was helpful to4 thankful Users |
8/11/2010 1:27 AM | |
Posts: 50 Rating: (0) |
ok thank you very much for your help! |
Last edited by: Ing. Hass at: 8/11/2010 1:27 AM |
|
This contribution was helpful to1 thankful Users |
9/17/2013 10:07 AM | |
Joined: 4/24/2009 Last visit: 8/2/2024 Posts: 2682 Rating: (135) |
New question was splitted to two RTU's needs to remotely communicates via GSM ( Requirement) with the central SCADA WinCC 7.0 Best regards O_Moderator |
12/15/2015 10:33 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4769 Rating: (123) |
New question published by Arucad is split to a separate thread with the subject Example for Modbus RTU setup in TIA. Best regards |
Follow us on