7/17/2012 11:25 AM | |
Posts: 10 Rating: (0) |
Hi True Heart, Can you goto online - PLC diagnotic to check both of the RAM of PLC. Regards, CHVoon
|
7/17/2012 11:31 AM | |
Joined: 10/3/2007 Last visit: 6/25/2024 Posts: 188 Rating: (34) |
Check if your CPU's have the exact same part number and firmware version. |
7/17/2012 1:24 PM | |
Posts: 4 Rating: (0) |
hi dmertens, CPU model nos and firmware versions are exactly same
|
Last edited by: TrueHeart at: 7/17/2012 1:25 PM |
|
7/21/2012 2:02 AM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309)
|
HelloTrueHeart,
You didn't mention something about memory cards and synch. modules. Please double check the part numbers and versions of the 4 synch. modules and also the memory cards. Can you try a small project with default CPU settings and a small program and download it to work memory of CPUs without memory cards? Do both CPUs work redundantly in this case? Can you swap synch.modules and see if CPU in Rack 0 is going to stop instead of CPU in rack 1? Best regards, H-H
|
This contribution was helpful to1 thankful Users |