3/24/2021 11:42 AM | |
Joined: 9/30/2016 Last visit: 4/5/2024 Posts: 910 Rating: (6) |
Please also see the attached screenshots. We have a machine where something that is/should be a warning (and in my opinion therefore activate the yellow lamp) is treated as an alarm and is activating the red lamp. Yellow lamp is on Q110.2 and red lamp is on Q110.3. I can see in the DB (SystemFunctionData) that DB1.DBX43.0 is AlarmListStatus.Alarm and DB1.DBX43.1 is AlarmListStatus.Warning. When I search in the "Alarm Logging" for the signal (EB3_W5_Q1_BP2) I can find both Deviation Alarm and Deviation Advarsel (Warning) to be set to be the message type "Alarm" and I suppose that is were it sets DB1.DBX43.0 (AlarmListStatus.Alarm) high - but where do I see/create the link between each message and either DB1.DBX43.0, DB1.DBX43.1 or perhaps a completely other pin in the DB? AttachmentEB3 Danseralarmer.zip (74 Downloads) |
3/25/2021 2:12 PM | |
Joined: 5/16/2014 Last visit: 9/12/2022 Posts: 7298 Rating: (2145)
|
Hello xmnj, I can not see in your screenshots what is configured for https://support.industry.siemens.com/cs/ww/en/view/109772961/82200466955 But every message class, message typ or message group can have
Georg Berghof |
PS: If this post did really help you, you may use the Rate-button |
|
3/26/2021 7:44 AM | |
Joined: 9/30/2016 Last visit: 4/5/2024 Posts: 910 Rating: (6) |
Hello Georg, Thank you for answering. I will try reading the info in the link you posted. But can you perhaps explain how I see if it IS configured with status tags and how I trace what activates both DB1.DBX43.0(AlarmListStatus.Alarm) and DB1.DBX43.1 (AlarmListStatus.Warning)?
|