3/26/2013 3:32 PM | |
Posts: 45 Rating: (0) |
hasler |
Last edited by: f.hamza at: 7/7/2013 7:37 PM |
|
3/27/2013 11:46 AM | |
Joined: 9/27/2006 Last visit: 9/25/2024 Posts: 12283 Rating: (2685) |
Hello mostref; Hastler is a maker of industrial measuring devices for the cement industry, like weight feeders, See www.hastler-int.com. If they have sold the instrument to FLShmidt for insertion in a larger machine, the program could have been developped by FLShmidt to include the weigh feeder station as one part of their product.So it is very difficult to say without more information what the details of the program are. You can generally load the Step 7program on either a S7-300or a S7-400 indifferently, the only requirements are memory size and capacity. There are a few communication blocks that were generated specially for S7-400, but loading these on a S7-300 would give you a system fault as soon as you would download the program. If the program uses instructions that address ACCU2 (only a S7-400 has the second accumulator in its configuration) the same thing would happen when downloading to a S7-300: a SF and STOP mode. But there would be no other damage. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 3/27/2013 11:47 AM |
|
This contribution was helpful to1 thankful Users |
3/30/2013 3:40 PM | |
Posts: 45 Rating: (0) |
but i'm using the S7-400 |
4/3/2013 4:28 PM | |
Posts: 836 Rating: (100)
|
well.... whats the problem then? |