5/29/2013 1:05 PM | |
Posts: 24 Rating: (0) |
Thanks for the info but it would be nice if you explain how to chnage the watchdog time of the dp slave on profibus. |
5/30/2013 12:45 PM | |
Posts: 24 Rating: (0) |
Hi Wizard, Thank you very much for the information. I am at site in china on commisioning, now a days i m doing crane application which is having 315-F plc and ET200S remote station which also contaion F_DI module. The plc is on the ground (Fixed) and the Remote station is on the crane (Movable), i established the wireless communication between them, but i am getting parameter assignment error on the safety module but dip switch setting is correct and F_Monitoring time i set to 5000ms just for testing but no improvment, still i m getting same error.The configuration printshot is attached and i also increased the update time of the profinet nodes. Then what else i am missing or we can not use fail safe module on wireless node ? Best Regards Ashish Singh AttachmentPrintShots.zip (198 Downloads) |
5/30/2013 3:04 PM | |
Joined: 4/24/2006 Last visit: 9/19/2024 Posts: 8739 Rating: (1168)
|
Hello, Have you seen this thread: /tf/WW/en/Posts/44857 and S7 Distributed Safety V5.4 and V5.4 + SP 1,2,3,4,5: Product Information on F Execution Times and F Monitoring and Response Times Best regards, Wizard |