2/16/2007 8:16 AM | |
Joined: 10/11/2006 Last visit: 4/24/2024 Posts: 5823 Rating: (789)
|
Attached is theterminal description for the 5kW SLM. The communication is done exclusively by the digital inputs/outputs. The control signals for the SLM (X22.2 disable regeneration and X22.3 reset faults) should be connected to digital outputs of the CU. The checkback signals of the SLM (X21.1 ready and X21.2 prewarning)should be connected to digital inputs of the CU. Regards, TechTeam AttachmentSLM.pdf (891 Downloads) |
With best regards, |
|
This contribution was helpful to1 thankful Users |
2/23/2007 10:35 AM | |
Joined: 10/11/2006 Last visit: 4/24/2024 Posts: 5823 Rating: (789)
|
Hello JAsVAp, did you take care about the sequence of the signals? ON/OFF1 should be given after all other enables are set. What is the status of r898 and r899 at the axis? For the start up we recommend the commisioning manual which can be find here: www.automation.siemens.com/doconweb Best regards TechTeam |
With best regards, |
|
9/10/2013 3:37 PM | |
Joined: 4/24/2009 Last visit: 2/19/2024 Posts: 2683 Rating: (135) |
New question was splitted to CU320-2 DP and SLM with 3 single motor modules Best regards O_Moderator |
Follow us on