1/19/2012 12:46 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685)
|
Hello Rajkiran; The 6ES7 331-7NF00-0AB0 can be wired for both 2-wire and 4-wire current transmitters. have a look at this extract rom the S7-300 Module Data manual. S7-300 Automation System Module Data Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
1/20/2012 4:18 PM | |
Joined: 7/2/2008 Last visit: 8/26/2024 Posts: 928 Rating: (308)
|
Hello RAJKIRAN, Just few words to add to the good reply of Daniel. Any 4-20mA will support both 2-wire connection and 4-wire connection but some modules (like the one you have) support the 2-wire connection but with external supply while some other modules support the 2-wire connection without external power supply. Best regards. H-H
Attachment2-wire.pdf (700 Downloads) |
This contribution was helpful to1 thankful Users |
12/13/2013 12:30 PM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating: (135) |
New question splitted to problem on using AI module Best regards O_Moderator |