10/7/2014 7:49 PM | |
Posts: 28 Rating: (0) |
Thanks ill give it a go |
This contribution was helpful to1 thankful Users |
10/8/2014 4:31 PM | |
Posts: 28 Rating: (0) |
thanks for that. Could you elaborate as to why the termination resistor need to be on both side please?
regards. Craig |
10/8/2014 5:23 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hi Craig, Please have a look: WBT PROFIBUS Installation Guide - 2 Assembling PROFIBUS cables Wrote: Termination prevents reflections that can disturb the data communication. The higher the baudrate and the longer the cable, the more important termination becomes. Termination should be activated/placed at both ends of every bus segment. With PROFIBUS DP the termination is powered to provide an idle level when nobody is sending data. |
Last edited by: Ste39 at: 10/8/2014 5:24 PM |
|
This contribution was helpful to1 thankful Users |
10/14/2014 11:33 AM | |
Posts: 28 Rating: (0) |
HI Using the siemens profibus plugs with both ends connected to the left hand side and the terminating resistors on I still cannot get it to connect to s7-200 PCU 266.( PLC port 0 and IF1B on screen.) I have uploaed a screen shot the the coms set up on pro tool. Thanks Attachmenttp170_mono_coms.pdf (216 Downloads) |
10/16/2014 12:46 PM | |
Posts: 28 Rating: (0) |
Hi Any takers for the above?? Help would be very my appreciated Thanks
|
10/16/2014 1:42 PM | |
Joined: 4/24/2006 Last visit: 9/20/2024 Posts: 8742 Rating: (1168)
|
Hello, Please check the address of S7-200 in system block. (Is it address 3?) Best regards, Wizard |
10/16/2014 3:12 PM | |
Posts: 28 Rating: (0) |
No ports 0 & 1 were address 2 . Changed port 0 to 3 and downloaded,screen now not giving plc disconnected alarm but can no longer download to plc? |
10/16/2014 3:38 PM | |
Joined: 4/24/2006 Last visit: 9/20/2024 Posts: 8742 Rating: (1168)
|
Hello, When using MicroWin, you make sure you are now looking for Remote address 3. Best regards, Wizard |