4/24/2017 11:29 AM | |
Joined: 7/30/2012 Last visit: 9/16/2024 Posts: 335 Rating: (12) |
Hi.. I'm using 1PH7103-2JF03-0BB0 Motor (HTL Encoder ) With Simotion and SMC30 I have Wired Encoder Cable As Per Siemens Manual (Reefer Picture ) But I'm Getting Error Temperature Sensor Fault If Change KTY84 To No Sensor in Parameter P601 Its Working Fine AttachmentSMC And Cable.zip (257 Downloads) |
4/26/2017 9:22 AM | |
Joined: 7/30/2012 Last visit: 9/16/2024 Posts: 335 Rating: (12) |
Hi.. Thanks For Your Reply Will Check And Revert Back |
4/30/2017 7:16 PM | |
Joined: 7/30/2012 Last visit: 9/16/2024 Posts: 335 Rating: (12) |
Hi.. Cable and parameters setting are as You said but still I'm getting Same error |
5/2/2017 12:02 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, so if you have already checked the KTY84 sensor itself, the parameter settings of p600, p601 and the wiring I would recommend to contact our customer support for further support. |