Hello, Did you connect the sensor as shown in picture,have a close look athow the compensation wire is connected . Have you seen this important note?
@Gabriel: 2,3 or 4 wire has nothing to do with powersupply, but all with compensation of wire recistance see: http://www.omega.com/temperature/pdf/rtd_gen_specs_ref.pdf Regards, Marcjan |
Last edited by: Marcjan at: 1/11/2012 9:55 AMProblem solved? |
|
6/27/2017 10:41 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by Pablo Rodríguez is split to a separate thread with the subject Connect RTD with 3 wires directly to analog inputs in PLC S7 1200. Best regards |