10/18/2017 2:35 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685) |
Hello; The fact that it seems that the S7-1500 does not support FF H1, it would seem that HART should be a better solution. In the Siemens world, FF H1 is only supported by the PCS7 environment, as you can see for Compact FF Link manual: For HART, you can use HART modules (AI, AO, AI-DI/DO) as part of a remote ET 200SP HA system. See the related documentation: SIMATIC ET 200SP HA Distributed I/O system SIMATIC ET 200SP Analog Input Module AI 16xI 2-wire HART HA SIMATIC ET 200SP HA analog output module AQ 8xI HART HA SIMATIC ET 200SP HA AI-DI 16/DQ16x24VDC HART Note that these modules are all point-to-point HART, HART multidrop is not supported. Hope thishelps, Daniel Chartier |
Last edited by: dchartier at: 10/19/2017 2:29:01 PM |
|