Dear
Sir, PCS7 V8.2 Wincc V4.0.0 AS Systems: 5 ,AS410-5H (FW8.2) OS servers : 1 Red. Pair (2 Servers) With Windows Server 2012 R2 x 64 Bit OS Clients : 10 with Windows 7 64 Bit ES : 1 with Windows 7 64 Bit We are
facing some critical problem of both Server’s user archive, which are not
getting synchronized many times. Due to
this, whenever Control Operator tries to modify recipe, it is not accepting
changes as the values are not able to write in user archive. At that
time we tried to open user archive’s data manually it shows an error “No Run time
Data Yet’’. (Please refer attached screenshot). We need to
open & close archive data 2-3 times on both servers, after that we are able
to see the archive data & CO is able to modify the recipe. Whenever we
download server after compilation, we are facing this problem every time &
sometimes it occurs randomly. Kindly
acknowledge & do needful to resolve this problem on priority basis. -------------------------------------------------------------------------- Warm Regards, Henish Chahwala ------------------------------------------------------------------------------------------ |
Last edited by: Henish_Chahwala at: 1/4/2018 5:56:08 AMLast edited by: Henish_Chahwala at: 1/4/2018 6:00:30 AMLast edited by: Henish_Chahwala at: 1/4/2018 6:04:04 AMLast edited by: CS Moderator at: 1/4/2018 11:39:22 AMNew subject after splitting |
|
1/4/2018 6:43 PM | |
Joined: 3/14/2008 Last visit: 9/23/2024 Posts: 2096 Rating: (938)
|
Hi, Please check if you have activated option: "allow activation on ES" in the server project on the ES. If so, problems like you describe can occur. Make sure you disable the option and download the project to the servers. Check again if problems occur. When this option is enabled and you are opening user archive editor on the ES, the user archive synchronization stops and the problem occurs. Simply opening the editor is enough to make user archives crash!! You can find the option under the WinCC project settings in WinCC explorer. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to2 thankful Users |
5/23/2022 8:04 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hi vishal p., sometime ago I had also the same problem. The Siemens support and I suggest that this had do with the OS server activation on the ES (I had once to activate the OS project on the ES to connect several 1500 controllers, read the tags and messages is only possible with active tag logging respectively alarm logging). After the activation of the OS server project on the ES I followed the FAQ What should you do if the OS server project is taken online by mistake on the ES? to repair the project on the ES. But at the commissioning we faced the same issue as in the topic described.
I hope this procedure can help you as well. With regards |