2/28/2018 6:43 AM | |
Joined: 3/14/2008 Last visit: 9/20/2024 Posts: 2095 Rating: (936)
|
Hi royalmaster, The interlock blocks do not have a message functionality so you have to use the external message signals available to your motor block (MotL, MotSpdL, MotSpdCL). You have three of them: ExtMsg1, 2 and 3. Take a look at the attachment, I have a similar situation. When one of the three interlocks is bypassed (Permit, Protect or Interlock), then I generate an external message at the motor block via ExtMsg01. I set a message class and alarm comment for SIG4, meaning ExtMsg01 (SIG5=ExtMsg02, SIG6=ExtMsg03). |
Last edited by: Oreca at: 2/28/2018 6:43:53 AMIf I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
2/28/2018 6:48 AM | |
Joined: 3/14/2008 Last visit: 9/20/2024 Posts: 2095 Rating: (936)
|
Or, you can use an alarm8p block to trigger messages. See the following attachment. I attached ExtMsg1 to the alarm8p block, configured the message and you have the same situation. The alarm 8p block is configured in the CFC, so when the message is triggered (only by positive trigger of ExtMsg1), the SOURCE column can display the CFC chart name as well (by default). So you will know where the alarm is coming from. PS. There are a few options more, but this is just to give you an idea how to work with messages. |
Last edited by: Oreca at: 2/28/2018 6:49:04 AMIf I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
Follow us on