9/20/2018 9:44 PM | |
Joined: 3/14/2008 Last visit: 9/20/2024 Posts: 2095 Rating: (936)
|
Hi, What you have to do is the following: 1. Go to WinCC explorer and open tag management. 2. Go to your internal tags and search for: "@APLCommandExecutionSteps". 3. Change the start value of that tag to "2". This means it is no longer necessary to confirm the value in the faceplate by clicking "OK". Values are applied immediately. Note: If you change it back to "3", the OK button should be pressed. This change will have effect on all APL faceplates.. If you don't want this, you need to make a copy of your faceplate and configure your own tag to hide or show the OK button.
|
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |