Kindly share GSD file of Power Focus 4000 (Atlas Copco Controller ) . I want to established Communication Between Power Focus 4000 and S7 1200 or S7 1500 CPU( Where PLS is Master) and PF 4000 is slave. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/28/2018 6:47:34 AMNew subject after splitting |
|
11/28/2018 7:54 AM | |
Joined: 7/9/2015 Last visit: 4/24/2024 Posts: 3812 Rating: (554)
|
Hi, I can give you a general answer for S7-PLCs Check compendium: CPU-CPU communication with SIMATIC controllers (compendium)Regards, Towome |
|
|
2/18/2022 7:15 PM | |
Joined: 10/30/2020 Last visit: 2/22/2022 Posts: 1 Rating: (0) |
hello, did you get the file? How did you finish the job, your project? |
2/18/2022 8:32 PM | |
Joined: 9/27/2006 Last visit: 4/25/2024 Posts: 12257 Rating: (2665)
|
Hello MiPersona; The answers provided to the original poster were correct, and the manual for the PF4000 confirms this. http://www.e-pneumatic.com/media/pdf/atlas-copco-power-focus-4000-manual.pdf On the PLC sid, you will need a Profibus master communication module, on the S7-1200 it would be a CM 1243-5: https://support.industry.siemens.com/cs/ww/en/view/49851842 On the S7-1500 you need a CM 1542-5: or a CP 1542-5: https://support.industry.siemens.com/cs/ww/en/view/109762507 https://support.industry.siemens.com/cs/ww/en/view/76894900 Hope this helps, Daniel Chartier |