12/3/2018 7:34 AM | |
Joined: 1/20/2017 Last visit: 3/17/2023 Posts: 2 Rating: (1) |
Hi all, Asking to Siemens Support, I found that this is a kwon issue of startdrive V15 and will be fixed in startdrive V15.1. As a workaround try this: - Disconnect the G120C drives from the PLC in the offline project, but don't delete them. - Install the gsd file for SINAMICS G120C, if not installed already. Link:https://support.industry.siemens.com/cs/ww/en/view/60292416 - Use GSD files for G120C drives to integrate them in TIA V15 -> insert the drives as GSD file from the HW catalogue from the folder "Other Field devices" set the same PROFIBUS addresses as for disconnected drive (as for Startdrive objects), connect the GSD drives with the PLC in the offline project, compile the HW config of the PLC and download it to the PLC. Use the Startdrive objects of the drive in the project only for a quick commissioning via usb cable. - Alternatively use TIA Startdrive V14 SP1 - there the communication works. Best Regards Andrea. |
This contribution was helpful to1 thankful Users |