Dear Willies, firstly the I Device functionality is not tested and not released with PCS 7. But technically it should not be a problem. Please mind that it is only possible to integrate the I device to a single CPU. It is not possible to integrate an I device to an redundant CPU (in a redundant way). CiR is probably not supported from the I device, but for your usecase you do not need CiR functionality in the i-device. If you have a CPU 410 with FW V8.2 and so on you can add and remove devices in Run. This is independent of the CiR functionality of the device itself. The CiR functionality of the device is only needed, if you want to change the configuration of the device in Run. If you have a configured topology and want to add a the i-device please mind that the device next to the i-device has to support CiR, because the topology configuration must be changed: https://support.industry.siemens.com/cs/ww/en/view/109749355 Have a look at chapter 5.1 of the following application example "PROFINET in SIMATIC PCS 7 V9.0 – Guidelines and Blueprints" for more Information about CiR: https://support.industry.siemens.com/cs/ww/en/view/72887082 |
Last edited by: 51N3P at: 1/28/2019 8:42:12 AMKind regards |
|