2/6/2019 4:30 PM | |
Joined: 3/14/2008 Last visit: 9/17/2024 Posts: 2095 Rating: (936)
|
Hi Kbv, To give you some more information: The maximum configuration of a PCS7 Smart system is as follows: - A maximum of 1 OS project in the multiproject - Maximum 2400 PO per OS project on one OS Single Station system - Up to 1 redundant single station with a maximum of 6 reference stations - Only CPU410 and CPU410 Smart can be used in the same project, no S7-400 - PCS7 Smart does not support client-server architectures The architecture can be as follows: 1. 1 OS Single Station up to 6 reference stations OR 2. 1 OS Single Station Redundant system * *The same project runs on each OS You can simulate OS on the ES, but you need a OS runtime license on the ES. You can use the CPU410 Smart in a standard PCS7 environment, but you need to download the HUP package and you must bear mark that it does not behave like a CPU410-5H, for example: - External DP interface not possible - External IO controller not possible - Using the Smart as fail safe is not possible - The maximum integrated memory is 8MB, 4MB for programs/4MB for data - OB2x are not supported - The following cyclic interrupts are supported: OB32/33/34/35 - OB4x are not supported - Minimum cycle time of OB1 is 200ms and cannot be changed - Ethernet interface X8 is designed as service interface and cannot be used Hope this helps you a bit |
Last edited by: Oreca at: 2/6/2019 4:40:32 PMIf I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to3 thankful Users |
2/26/2019 8:58 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hello Kbv, the standard software is only available over the DVDs. Only updates are available as download. The only solution I know is to contact your local siemens contact under https://www.automation.siemens.com/aspa_app/?ci=yes&lang=en. With regards |
This contribution was helpful to1 thankful Users |
Follow us on