3/5/2019 2:09 PM | |
Joined: 3/14/2008 Last visit: 9/23/2024 Posts: 2096 Rating: (938)
|
Hi, This means that the I/O cannot be monitored online (The maximum is exceeded). If you remove some I/O-> Right click on I/O and select: "Remove I/O" or just right click on a block and select: "Watch Off", then it may be possible to monitor the values. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
3/6/2019 12:15 PM | |
Joined: 9/9/2015 Last visit: 9/15/2024 Posts: 727 Rating: (278) |
Dear OMKRIS2017, You may have monitored too many IO in one shot. try close some charts, or remove some IOs to be watched on. If CPU performance is not your concern, you may try to turn Laboratory view on. (CFC editor -> Debug-> Laboratory mode) - This allow you to turn everything in to watch on in one shot. Normally helpful during commissioning. Will not solve your Red IO issue, but is a good to know features for your info. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|