Hello Everyone, my motorised valve is a VULPES POSI range, , i join the technical documentation of the valve page 21 in english, page 9 in french, tell me the information that must be attached to be clear on my question AttachmentDSBA1430 Doc tech comm ER PLUS.pdf (259 Downloads) |
Last edited by: autokabyl at: 05/02/2019 14:52:21 |
|
5/2/2019 3:20 PM | |
Joined: 9/27/2006 Last visit: 9/24/2024 Posts: 12282 Rating: (2685) |
Hello Autokabyl; Based on the document you provided, it seems the POSI version of your valve actuator will take different positions based on the analog signal you produce. The actuator works linearly, and will remain in its last position upon loss of power or control signal. For a 4-20 mA control signal from your analog output module, - at 20 mA the valve will open fully (100%) - at 12 mA, the valve will open/close to 50% open - at 0 mA, the valve will move to a fully closed position (0%). - for other values of the control signal the valve will place itself at a position corresponding to the value of the control signal. So, you must learn to use the NORM_X and SCALE_X instructions to configure your analog output to provide a signal of 0-100% (engineering values)-> 4-20mA (current output) -> 0-27648 (for native analog output numeric values), as Huggy_DI suggested earlier. Use the Step 7 online help to get the basic information on these functions, and study Example 2 in the following document to see how to get a 4-20 mA control output to your valve actuator. For an S7-1200/S7-1500 controller in STEP 7 (TIA Portal), how do you scale integer values in real numbers and vice versa for analog inputs and outputs? https://support.industry.siemens.com/cs/us/en/view/39334504 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 05/02/2019 15:40:17 |
|
This contribution was helpful to2 thankful Users |
Follow us on