9/16/2016 7:01 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Please check below FAQ, may be useful to you. Which interface modules can you use with the modules of the ET 200SP "TM Count 1x24V" and "TM PosInput 1"? |
9/19/2016 1:05 PM | |
Joined: 1/15/2016 Last visit: 9/11/2024 Posts: 178 Rating: (4) |
Thank you for the answer, but this is not exactly what I was looking for. I need to know how to use this module ET200SP with Step 7 SIMATIC Manager V5.5 SP4. I am NOT using TIA Portal V13. Thanks. |
9/19/2016 11:32 PM | |
Joined: 4/28/2015 Last visit: 1/24/2022 Posts: 1 Rating: (2) |
Hi, the support from Siemens just answerd me today almost the same question but I didn't tried yet. They told me that the module can be either use to measure the value or to count a value, not both at the same time and this is parameterized on the hardware configuration. Please open the Manual TM Counter and see that on page 27 and 28 has the data that you send (always set SW_GATE = 1 to enable the use) and on page 29 has the received data that you can read (Check if STS_SW_GATE = 1 that means enable to be used), and depends on your choise you can use this data: Bytes 0 to 3 COUNT VALUE Current counter value Bytes 4 to 7 CAPTURED VALUE The last acquired Capture value Bytes 8 to 11 MEASURED VALUE Current measured value. I can help you until here only. Good lucky, Best Regards. |
9/21/2016 1:26 PM | |
Joined: 1/15/2016 Last visit: 9/11/2024 Posts: 178 Rating: (4) |
Thank you all for the answers. |