Hello wmacca; If your plan is to simply remove the S7-300 CPU from th rack and replace it with a S7-1500 CPU, to control the S7-300 I/O modules, you will find you cannot do so. What you can do is install the S7-1500 CPU on its own rack, replace the S7-300 CPU with a IM module (IM 153-2 for Profibus, IM 153-4 for Profinet) and transform the S7-300 rack into a ET 200M distributed I/O station that you can control over a fieldbus, either Profibus or Profinet. This link may provide some basic information: This migration guixe will show you hints about connecting ET 200M stations to a S7-1500 IO-controller, in chapter 4: https://support.industry.siemens.com/cs/us/en/view/109478811 Hope this helps, Daniel Chartier |