6/17/2019 11:39 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684)
|
Hello shafid: The CPU you show is a IM 151-8F, 6ES7151-8BF01-0AB0. The technical data of the CPU (you can locate it rather easily, put the part number in the Search Box at the right of this page, and open the Product Link in the results page) shows that the engineering package required is Step 7 v5.5, plus Distributed Safety V5.4 SP4 (if you have a Safety program in the CPU). https://support.industry.siemens.com/cs/pd/390575?pdti=td&dl=en&lc=en-WW Here is the manual for Step 7 v5.5, chapter 19 is decdicated to Download and Upload of the CPU program; no symbol cor comments are available for upload, though. Programming with Step 7 v5.5 : https://support.industry.siemens.com/cs/ww/en/view/45531107 Here is the manual for Distributed Safety. Nope in section 10.4 that uploading the Safety program will not result in an editable file in your PC, since no symbol information is saved on the PLC. You can transfer this Safety program to a new CPU, but not edit it. You need the original program to work with it. Distributed Safety v5.4 : https://support.industry.siemens.com/cs/ww/en/view/22099875 hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
7/5/2019 12:16 PM | |
Joined: 12/25/2018 Last visit: 9/17/2024 Posts: 76 Rating: (0) |
thank you so much for the detailed answer |