Posts: 17 Rating: (0) |
------------------------------------------------------------------------------------------ AttachmentMotor_runs_only_once.pdf (49 Downloads) |
||
Last edited by: Jen_Moderator at: 07/24/2019 08:46:19New subject after splitting |
|||
7/24/2019 11:06 PM | |||
Joined: 7/7/2010 Last visit: 9/23/2024 Posts: 15217 Rating: (2417)
|
You need a state machine or sequencer to manage the various activities of the required logic. Network 1 only needs to run after something requires reset. Instead, it is resetting every scan, which on an s7-1500 is very fast. The forward operation and reverse operation should be managed with a time delay between them to protect the motor.
|
||
science guy |
|||
This contribution was helpful to1 thankful Users |
7/26/2019 9:34 AM | |
Posts: 17 Rating: (0) |
Thank you for the information but I am completely new to PLC programming how one can implement state machine in ladder logic.? |