9/3/2019 7:12 AM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (298) |
Hello, first of all: You are completely right -> S210 is designed for S7-1500 PLCs. The problem with 1200 PLC is that it does not support IRT (isochronous communication). This can lead to bad control behavior, especially because the S210 has very fast internal controller cycles. So I cannot recommend the solution with S7-1200 at all! BUT: If you now have it and you cannot avoid the solution I want you to know some hints. Please find the attached PDF with a description of what can improve the control behavior. E.g. doing the One Button Tuning only with presetting "conservative". And also check out the cycle times and speed setpoint filters that should be set. So please upgrade your S210 to the latest firmware! And please check the points in the file attached! Otherwise you can have bad control behavior and you will hear that in your mechanics! The SD card probably will be for the S210, the only license actually is the Safety Extended license, so this should be on the card. Only with this license you can use the extended safety functions in the drive. AttachmentS210_at_1200_restrictions.pdf (1487 Downloads) |
Last edited by: RB91 at: 09/03/2019 07:12:47Best regards, |
|
This contribution was helpful to6 thankful Users |