10/12/2019 5:41 PM | |
Joined: 9/27/2006 Last visit: 9/23/2024 Posts: 12282 Rating: (2685) |
Hello; Could you give us the part number of the S7-415H you are working with? It is not available under that designation under Product Support, it might be an older model, no longer produced. Meanwhile, have a look at de technical data of the S7-414-5H CPU, the newest mdoel available. I doubt that an older model would do things differently that the most up to date CPU: https://support.industry.siemens.com/cs/pd/252539?pdti=td&dl=en&lc=en-WW Roll down to the section named "2.Interface", for the integrated Profinet ports. They are described as 2 Ports, 1 integrated switch. This means that you cannot put a different IP address on each port, the are connected by the internal swtch to facilitate a line structure. I feel it must be the same for your own CPU. Hope this helps, |
10/12/2019 5:54 PM | |
Posts: 25 Rating: (2) |
Thank you dchartier for reply |
10/12/2019 6:41 PM | |
Joined: 9/27/2006 Last visit: 9/23/2024 Posts: 12282 Rating: (2685) |
Hello; So, you are actually working with a CPU 412-5H CPU, one of the latest models ( actually, the most recent version). https://support.industry.siemens.com/cs/pd/53296?pdti=td&dl=en&lc=en-WW You can see from the technical data that it is the same as for the earlier CPU data I showed: your CPU has 2 integrated Profinet ports, connected by an internal switch. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 10/12/2019 18:43:54 |
|
10/13/2019 11:10 AM | |
Posts: 25 Rating: (2) |
Thank you dchartier, This was so helpful |