Hello Eemuhendisi; You are right, the manuals of the IPC427C show only a "Group error" designation for the SF LED of the Microbox, without more explanation; that means any combination of events is lumped together with this LED, and you need further diagnostic tools. Note that there is a SF for Profinet on the Microbox also, with specific diagnostic information. This diagnostic package should provide you with more information on the source of the "Group error" on your Microbox: SIMATIC IPC DiagBase - Download Since the screen (possibly your video card) is your problem, you might not be able to use the diagnostic tool efficiently. In that case I would suggest you open a Support Request ( use the link at the top of this page and have all the technical information on your system available, including exact part numbers); this would get you in contact with a Siemens tech who should be able to help you out. Hope this helps, Daniel Chartier |