1/7/2020 9:54 AM | |
Joined: 8/20/2016 Last visit: 8/23/2024 Posts: 82 Rating: (0) |
I use in FC3 in attached file, but I only force PID operarte at MAN mode, when PID is not MAN mode nothing happen at PIW306. What I have set for it operate automatic. Thank you. Attachmentdotrac-CPU315.zip (245 Downloads) |
1/7/2020 10:04 AM | |
Joined: 7/9/2015 Last visit: 9/24/2024 Posts: 3943 Rating: (586)
|
Hi, you have to call you fc3 in OB35 and then set correct cycle time. After PLC Restart you have to set COM_REST for one plc cycle. Check manual for Cont_C and this FAQ for more Details: Where can you find descriptions and examples of PID control with FB 41, FB 42 and FB 43, and SFB 41, SFB 42 and SFB 43?What should you watch out for when calling and assigning parameters to the controller functions in function blocks (S)FB41, (S)FB42 and (S)FB43?Regards, Towome |
|
|
This contribution was helpful to2 thankful Users |