3/1/2020 10:21 AM | |
Joined: 4/28/2017 Last visit: 3/14/2024 Posts: 149 Rating: (24) |
Hello amirab, The steps to take a PCS7 H system project into PLC sim simulations are defined, 1. Modify your Netpro connection, Create TCP/IP or ISO connection between AS and OS, 2. Compile OS with changes only scope, 3. Open WinCC explorer, Proceed to Tag management, Then browse into the property of "TCP/IP Connection" - Use connection type as "PLCSIM" (Network card selection). Update PLM IP address and rack number under created new connection type. 4. Launch PLC SIM, and choose the right network type (ISO or TCP/IP) Download the HWconfig of CPU by choosing the particular rack of what you selected in Netpro 5. Download your Charts as program 6. Activate WinCC runtime, Then, verify your connection. Since you have mentioned as you could create the connection during mentioning rack 02 in the new network connection, I think either you might have download the wrong rack to PLC sim or the rack used to create a Netpro connection would be another. Please verify it. Also, read the below steps. it may be helpful to you... How do you use S7-PLCSIM with SIMATIC PCS 7? PCS7 V8.1 OS communication with PLCSIM |
Last edited by: Jen_Moderator at: 03/02/2020 11:45:59Optimized link. Note: If this post did really help you, you may use the "Rate" button to express your support, Thank you. |
|
This contribution was helpful to1 thankful Users |
3/1/2020 12:59 PM | |
Joined: 12/16/2018 Last visit: 6/16/2024 Posts: 67 Rating: (0) |
Thanks for your reply but as mentioned in the last line I'm having trouble communicating with TCP/IP (also ISO) connection and going through exactly the same process but at wincc with the main rack connection under which the tags are also built I don't have but okay with Rack 1. Also, when I connect CPU and OS to the MPI network, it communicates in wincc is established. |
Last edited by: amirab at: 03/01/2020 13:03:13Last edited by: amirab at: 03/01/2020 14:02:48 |
|
3/1/2020 8:45 PM | |
Joined: 12/16/2018 Last visit: 6/16/2024 Posts: 67 Rating: (0) |
please see attachment AttachmentImages.zip (71 Downloads) |
3/2/2020 12:34 PM | |
Joined: 4/28/2017 Last visit: 3/14/2024 Posts: 149 Rating: (24) |
Hello amirab, I was gone through your images. It looks good. But, Can you please try one thing ..??? Please choose your AS station in Netpro (your picture no.02) and in the available connection list, Right-click on your AS-OS connection and choose "Download selected connection". Give a try. It may work as I hope. Do the same by choosing your OS station and perform connection download (Download selected connection), It seems to be only a connection related issue, it may work if you download the Netpro after hardware and Charts download. Also, one more suggestion for you. When you are using FB_UA_RM tags under PLC sim the data type should be mentioned properly. I couldn't see it in your image. Just ensure that you have chosen the right one (Please refer to my attached images). AttachmentPLC_SIM_OS_Config.zip (57 Downloads) |
Note: If this post did really help you, you may use the "Rate" button to express your support, Thank you. |
|
3/3/2020 8:28 AM | |
Joined: 12/16/2018 Last visit: 6/16/2024 Posts: 67 Rating: (0) |
Hello and thank you for your guidance. AttachmentImages.zip (90 Downloads) |
3/3/2020 7:00 PM | |
Joined: 4/28/2017 Last visit: 3/14/2024 Posts: 149 Rating: (24) |
Hai amirab, I'm sorry. I couldn't predict what could be the problem over conversations. I had never faced such issues even after working with many PCS 7 version in simulation, But, you said you could communicate with rack 01. So, it wouldn't be a problem with the PCS7 version as a bug. If you are eager to know the error, please Raise a support request to siemens. you will be knowing the exact issue at the end. Have a good time... |
Last edited by: Maruthakasi_S at: 03/03/2020 19:05:09Last edited by: Maruthakasi_S at: 03/03/2020 19:13:39Note: If this post did really help you, you may use the "Rate" button to express your support, Thank you. |
|
This contribution was helpful to1 thankful Users |