Hello imnlogo; First, about your counters. Do you mean you want to add the counters's actual value from the CPU1 and show them in CPU2? You could add the CV of each counters in CPU1 and send the resulting value to CPU2, or send the individual CVs to CPU2 and add them there. Next, how do you want to connect the 2 S7-1200 CPUs? The S7-1200 support Profinet communications natively, so the easiest would be to set CPU1 as IO Controller and CPU2 as i-device. If interested have a look at this Application Example: https://support.industry.siemens.com/cs/ww/en/view/109478798 Note that the IO Controller in the example is a S7-1500, but the settings are the same for a S7-1200. Hope this helps, Daniel Chartier |
4/9/2020 2:06 PM | |
Joined: 8/3/2009 Last visit: 9/20/2024 Posts: 13753 Rating: (1735) |
Hello here are the basics about PLC Communication: https://support.industry.siemens.com/cs/de/en/view/78028908 Page 106 Bye Murof |