4/7/2020 12:36 AM | |
Joined: 7/20/2006 Last visit: 8/21/2024 Posts: 128 Rating: (8) |
Hi, There is a way to reconnect block contact in SFC instance? When you made a mistake and connect block contact to eg. wrong valve, there is a way to reconnect it without removing interconnection manually? regards Edek ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 04/07/2020 09:12:53New subject after splitting |
|
4/7/2020 3:47 AM | |
Joined: 9/9/2015 Last visit: 9/25/2024 Posts: 727 Rating: (278) |
Dear edek, My way of doing is, 1. open up the block properties of SFC type instance, 2. set all the sfc block contact for that valve from invisible to visible, 3. delete them (wrong connection) manually at cfc. 4. reconnect the correct valve by clicking any empty input/output of the sfc block to the correct valve input/output. 5. done. You can also set those input/output to parameter and delete the textual interconnection in Process object view, but this is not the way i prefered which take up too much time. Hope this is helpful for u. |
Last edited by: JazTai at: 04/07/2020 03:48:07Please give me 5 stars Rating if my post is helpful for you. :) |
|
This contribution was helpful to1 thankful Users |
4/7/2020 7:51 AM | |
Joined: 3/14/2008 Last visit: 9/25/2024 Posts: 2097 Rating: (938)
|
Hi, A faster way is to make a copy of the block contact and delete the original. All connections are lost. Then rename the copy to the original and close interconnections. Now you need to assign the correct CM. This can be done for SFC types in general. But when using the new concept: EPHT/EMT (Equipment Phase Types and Equipment Module Types), this procedure is far simpeler because you define roles up front and when instancing in the project, you can assign the necessary instances to those roles and unassign them again. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to2 thankful Users |