6/26/2020 4:06 PM | |
Joined: 9/9/2015 Last visit: 9/15/2024 Posts: 727 Rating: (278) |
Dear Ahmed, Will it be software issue? have you checked your AS-OS software and Library are up to date? PCS 7 V9.0 SP2 Software Update Hope this is helpful for you. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
6/26/2020 4:29 PM | |
Joined: 11/10/2010 Last visit: 8/29/2024 Posts: 170 Rating: (9) |
thank you for answer JazTai, the SFC type was developped with PCS7 v 8.0, now i want to use it in a new project with PCS7 9.0 Sp1. so i updated the Old project to V9.0 sp1, and i copied the SFC type from chart folder to the chart folder of the new project, when i try to compile the SFC type or the SFC instance called in CFC i have this error.
|
6/26/2020 9:58 PM | |
Joined: 2/1/2010 Last visit: 9/19/2024 Posts: 150 Rating: (71) |
Errors can happen if you copy an SFC type from one project to another if the FB number assigned to the SFC type overlaps with one that you've already used in the new project. I can't recall if the error number you said is the exact one generated or not, but would be worth checking. I've had this happen and then the master data library gets corrupted for the block number and then both SFC types need moved to new associated FB numbers. If you do find it overlaps, it might be worth restoring your old master data library before you try to paste again. |
If my post helped you, please rate. Thanks. |
|