8/4/2020 8:17 PM | |
Joined: 9/27/2006 Last visit: 9/20/2024 Posts: 12282 Rating: (2684) |
Hello fsgonzaga; When you mention a redundant plant, you mean one designed around a S7-400H redundant controller pair, correct? In that case, you can establish redundant connections to a WinCC PC using Fault-tolerant S7 connections; you would need one (or 2, depending on the degree or redundancy required by your project) CP 1613 or CP 1623 in the WinCC PC, and a Redconnect software license. If you choose not to configure redundant connections to your WinCC application, you can use a standard NIC and non-redundant connections, but you will have to switch connections manually when the redundant CPUs do a switchover Fault-tolerant S7 connections are explained on the following document, along with the procedures to configure and use them: https://support.industry.siemens.com/cs/ww/en/view/16667714 Hope this helps, |
Last edited by: dchartier at: 08/04/2020 20:18:18 |
|
8/5/2020 2:09 PM | |
Joined: 8/3/2017 Last visit: 8/30/2024 Posts: 142 Rating: (0) |
Hello Daniel, thanks for the fast reply! Thats right. It´s a pair of S7-400H. In this case you mentioned, its better to use one CP for each WinCC PC? Regards.
|