10/29/2020 7:20 PM | |
Posts: 3 Rating: (0) |
Wow, so i just figured out could do this... I Didn't realize i could monitor the DB when online. I have gone through the configuration of the sensor about 20x now... it is a Keyence FD-Q20C. We have it configured as a 4-20mA. The Bioplar pin is set to false, the bias value appears to be 0. The HMI is reporting a flow rate of 0.2 gpm while the display on the Keynce is showing a flow of ~4.2 gpm. The 4.2 is much more realistic than the 0.2. |
Last edited by: Reegs at: 10/29/2020 19:21:46 |
|
10/29/2020 7:53 PM | |
Joined: 3/30/2020 Last visit: 9/23/2024 Posts: 4782 Rating: (982) |
I have the answer for you!! SP_Lim_Lo is set to an illegal number. This result in the SCALE_X not doing its job properly. This function pushes the normalized input through onto the output unchanged. Setting SP_Lim_Lo to "0.0" will solve your problem. Regards. |
Last edited by: qwazee at: 10/30/2020 05:39:45add motivation for solution Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to3 thankful Users |
10/30/2020 12:02 PM | |
Posts: 3 Rating: (0) |
This fixed the problem. Thank you!! |
This contribution was helpful to1 thankful Users |