Joined: 8/27/2020 Last visit: 9/16/2023 Posts: 4 Rating: (0) |
Hi. I have g120 240cu Siemens Drive and I Have two problems. 1:AI1 comes from plc (4-20mA) for speed setpoint. But the drive doesn’t receive this setpoint and setpoint doesn’t change. While I have changed DIP switches and P0756. Do I have to change another parameter? 2:I also can not start the drive with relay that are connected to the drive? Can you Help me? ------------------------------------------------------------------------------------------ |
Last edited by: Mahzad at: 11/19/2020 20:51:54Last edited by: Jen_Moderator at: 11/20/2020 09:59:52New subject after splitting |
|
11/20/2020 12:51 PM | |
Joined: 8/27/2020 Last visit: 9/16/2023 Posts: 4 Rating: (0) |
and also this. Thank you. |
11/20/2020 1:33 PM | |
Joined: 1/31/2013 Last visit: 9/13/2024 Posts: 34 Rating: (0) |
Have you checked p1000 and p0700?
|
11/20/2020 6:38 PM | |
Joined: 8/27/2020 Last visit: 9/16/2023 Posts: 4 Rating: (0) |
No.I haven’t. What value should I set them?( I mean P1000 & P700)
|
11/25/2020 9:35 AM | |
Joined: 1/31/2013 Last visit: 9/13/2024 Posts: 34 Rating: (0) |
Select Analog Setpoint in p1000 and control must be in terminals.
|