Industry Online Support
Technical Forum
4/9/2012 10:25 PM | |
Joined: 9/27/2006 Last visit: 9/25/2024 Posts: 12283 Rating: (2685) |
Hello Francisco; Here you will find information on how to connect a S150 drive to a PLC over Profibus-DP, how towire it, parametrize it and how to control it in the PLC program: Operating instructions for the S150 (Chapter 6.6: Profibus): SINAMICS S150; Converter Cabinet Units, 75 kW ... 1200 kW; Software Version 2.2 Noter:the manual is also downloadable in Spanish. GSD file (for integration in Simatic Manager, in order to communicate between the PLC and the drive over Profibus-DP): SINAMICS S120/S150, G130/G150, GM150/GL150/SL150/SM120, DCM: PROFIBUS GSD file However, if this is the first time you work with a drive on Profibus, you might find the reading difficult. You might want to look at some applications developped by Siemens, for S110, S120 drives over Profibus, and then adapt the program on S150 specific parameters and telegrams (as described in the Operating Instructions manual above). This would help you understand the mechanisms involved in controlling the drive http://support.automation.siemens.com/WW/view/en/34677186/136000&cspltfrm=0&cssw=0&csbinh=8 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 4/9/2012 10:28 PMLast edited by: dchartier at: 4/9/2012 10:26 PM |
|
Follow us on