11/1/2016 3:06 PM | |
Joined: 5/1/2013 Last visit: 1/22/2025 Posts: 428 Rating:
|
Hello What is isochronous mode mode and When we use this? Thank you. |
11/1/2016 6:32 PM | |
Joined: 3/28/2015 Last visit: 9/14/2025 Posts: 725 Rating:
|
Hello, Kindly have a look at the attached file. Isochronous mode with PROFINET Overview: The isochronous mode is always used in the SIMATIC S7-1500 when multiple parameter values which are comparable or in a relationship to one another are to be processed in one cycle. This requirement is fulfilled, for example, in the following scenarios. Simultaneous acquisition of multiple measured values which are to be acquired via various input modules. Execution of control processes on the SIMATIC S7-1500 CPU in which the acquisition of the measured values and output of the actuator signals is via various modules. Coherent control of multiple drives via the drive functions integrated in the SIMATIC S7-1500. Function: The coherent acquisition of multiple measured values in one program cycle is taken as an example for demonstrating the isochronous mode. AttachmentIsochronous mode with PROFINET.pdf (992 Downloads) |
Eng.Mohamed Ibrahim |
|
11/2/2016 12:10 AM | |
Joined: 2/3/2011 Last visit: 6/10/2025 Posts: 348 Rating:
|
Also used for Profibus, Chapter 5: |
Last edited by: syd_b at: 11/2/2016 12:15:33 AM |
|