10/30/2019 1:30 AM | |
Posts: 50 Rating: (0) |
Sir, We are using siemens 6ra70 drives,we are run single motor with help of two siemSie 6ra70 drives Running parallel (master,slave),these drives controlled by profibus DP. If possible based upon single drive shall we run the Motor . Please guide me. Thanks you sir. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/30/2019 11:44:50New subject after splitting Last edited by: Jen_Moderator at: 10/30/2019 14:05:47Optimized headline. |
|
10/30/2019 12:44 PM | |
Posts: 61 Rating: (1) |
HI, I think that you are using a master slave simoreg to control a single motor due to current issues. If you disable the slave equipment, I believe that you'll damage the master one due to overcurrent. Give us more information about your equipment. Hope it helps.
|
9/11/2021 8:08 PM | |
Joined: 8/2/2018 Last visit: 8/23/2024 Posts: 10 Rating: (0) |
Hi You can run only one drive if the current capacity of single drive (master ) can take the full load for the application from Minimum Tension to Maximum Tension ( Max Dia). The peer to peer documentation is enclosed. Hope this helps. Regards Sanjaya Srivastava [snip] Attachmentmaster-slave-switchover.pdf (793 Downloads) |
Last edited by: Jen_Moderator at: 09/13/2021 09:19:48Removed Contact data, doesn't comply with forum terms. Regards |
|