6/17/2014 8:22 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello adrian_botez Of course you can use the High Speed counters of CPU 314C CPU to measure Motor speed with an Inductive Sensor. You should however check the maximum switching speed of the Inductive sensor. An optical sensor may be better suited. Here is the Manual for Technological Function of Compact CPUs ( Including counting ) SIMATIC S7-300 CPU 31xC Technological Functions and an Example : SIMATIC S7-300 Getting Started - Commissioning a CPU 31xC: Counting Hope this helps Cheers Navnag |
Last edited by: Navnag at: 6/17/2014 8:23 PMThere is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
6/17/2014 9:00 PM | |
Joined: 2/19/2013 Last visit: 8/20/2024 Posts: 184 Rating: (9) |
But is there any formula to convert encoder pulses to length? |
6/18/2014 8:25 AM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804) |
Hello, normally motor with encoder is operated by a drive, e.g. Sinamics G120 or Sinamics S120, and thedrive has a interface for the encoder. http://www.industry.siemens.com/drives/global/en/converter/low-voltage-drives/Pages/Default.aspx |
With best regards, |
|
6/18/2014 8:40 AM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello adrian_botez You Need to calculate the Length / Distance for 1 motor Revolutionfrom the Mechanical data / Gear ratio etc. Distance per Encoder Pulse = Distance per Motor Revolution / Encoder Pulses Per revolution. Total Length / Distance = Cumulative No of pulses * Distance per Encoder Pulse Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|