4/6/2018 5:34 PM | |
Posts: 1 Rating: (0) |
Hello! i am newbie here! Can you tell me why Ics depends on voltage..and Icw doesnt? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 4/9/2018 10:31:38 AMNew subject after splitting |
5/4/2018 5:20 PM | |
Posts: 66 Rating: (4) |
Dearmiro86, Siemens provides pretty good planning manuals on https://www.siemens.com/global/en/home/products/energy/services/transmission-distribution-smart-grid/consulting-and-planning/tip-consultant-support.html. Please find attached a few pages out of the “Technical principles of power distribution planning” explaining the relevant criteria for circuit breakers. Ics is breaking capacity: To interrupt short-circuit current causes an arc over the contacts and arc quenching becomes more difficult on higher voltage. Icw is short-time withstand capacity: More or less power loss of a switching device or a busbar during short circuit, depends on the current and the resistance. Best regards SENTRONIX Attachment7_1_CircuitBreakers.pdf (1243 Downloads) |
This contribution was helpful to2 thankful Users |
7/29/2018 12:13 PM | |
Joined: 7/9/2014 Last visit: 9/6/2022 Posts: 6 Rating: (0) |
thanks so much |