5/7/2021 2:27 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello ashadako; Probaby because the user Engineer has been attributed the right to visualize the SFC, whereas the user Operator has not. User rights are planned and organized through User Administration. - How do the user rights (user authorizations) function in SIMATIC PCS 7? https://support.industry.siemens.com/cs/ww/en/view/60575347 From your description it seems that user administration is creating the PCS 7 users as part of the Windows administrative tools. One way to o thisis an ad-on callen Simatic Logon, do you knw whether it i installed on your ES? Hope ths helps, Daniel Chartier |
Last edited by: dchartier at: 05/07/2021 14:36:12 |
|
This contribution was helpful to2 thankful Users |
5/7/2021 3:21 PM | |
Joined: 8/1/2019 Last visit: 9/17/2024 Posts: 300 Rating: (3) |
Yes we use simatic logon. Its installed on all servers, clients and ES. Im still not sure where I should look. |
5/8/2021 8:05 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello ashadako; It has been a long time since I have done something like this, so bear with me if my explanations are not to date. SFC visualization is an OCX control that you insert in a WinCC (PCS 7) graphic page. The screenshot below is taken from the PCS 7 SFC Visualization v9.0 manual: https://support.industry.siemens.com/cs/ww/en/view/109748702 Check in your OS project if the Engineer has access to the graphic page where the SFC Visualisation control has been installed, and the Operator has not. Open the User Administration coniguration pages to do so. Hope this helps, |
This contribution was helpful to1 thankful Users |