5/10/2021 7:42 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hello PLC2011, you can configure the numbers of decimal point at the blockicon of the APL-block. Under "Object Properties > Properties > Configurations" you can find the settings "AnalogValueFormat1"... "AnalogyValueFormat5". With this settings you can configure how the values at the blockicon and faceplate is displayed. By the OpAnL is the "AnalogValueFormat1" for the PV-Value and "AnalogValueFormat2" for the SP-Value. For more information see the manual Advanced Process Library at the section Format specification for the analog value display. With regards |
5/10/2021 8:12 AM | |
Posts: 198 Rating: (60) |
Hello PLC2011, This can be done by changing the following properties of the block icon in the Graphic designer: Open the relevant picture in the graphic designer and select the OpAns block icon. Select 'Configurations' in the object properties window. Select the Analog format value option and change the number of decimals from 2 to 3.( ##0.000 ). I've also attached a screenshot for reference. Also it is to be noted that the analog value display formatting is taken centrally but it can be customized on a need basis using the attribute configurations listed above. If you would like to know about the applicability of this value display configurations across the parameters of other blocks, please refer section 'Format specification for the analog value display' in the APL Manual |
Last edited by: Jen_Moderator at: 05/10/2021 14:02:03Optimized link. |
|