5/20/2021 12:02 PM | |
Joined: 4/24/2006 Last visit: 9/20/2024 Posts: 8742 Rating: (1168) |
Hello, You need a Memory Card . Best regards, Wizard |
This contribution was helpful to1 thankful Users |
5/20/2021 12:02 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715) |
Hello, SIMATIC Memory Card required is stated here: 6ES7510-1SJ01-0AB0 Regards, Marcjan |
Problem solved? |
|
This contribution was helpful to1 thankful Users |
5/20/2021 9:49 PM | |
Joined: 2/17/2020 Last visit: 9/20/2024 Posts: 1062 Rating: (192) |
Hi Ivan_01, In addition to needing the memory card, as Wizard and Marcjan have told you, I would like to tell you about the existing firmware version differences. Firmware version 2.8.3, as you will be able to see in the following link, requires STEP 7 Professional V16 or higher. Firmware update S7-1500 CPUs incl. Displays and ET 200 CPUs (ET 200SP, ET 200pro) However, you can try to configure the maximum allowed in STEP 7 Professional V15 and check if you get a warning or an error when loading. Generally, having a higher physical firmware version than the configured one generates warnings that can be accepted and continue with the load. The only limitation is that you will not be able to count on the added functionalities of the higher firmware version. Hope it helps.
|
A rating will be well appreciated. |
|
This contribution was helpful to3 thankful Users |
5/25/2021 1:50 PM | |
Joined: 3/11/2019 Last visit: 9/6/2024 Posts: 1569 Rating: (289) |
Dear Ivan_01, as an addition, there is also a FAQ available. How do you load the project data if the version of the firmware installed in the S7-1500 CPU cannot be selected in the hardware catalog of your version of STEP 7 (TIA Portal)?
regards sancruz |
Feedback appreciated, please rate |
|