6/12/2021 3:28 PM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33820 Rating: (4203) |
If it is "top urgent" then call the Siemens hotline. |
This contribution was helpful to1 thankful Users |
6/13/2021 1:44 AM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685) |
Hello Tigranes; Information on the PMU 330BTE is difficult to come by LG-IS seen tp limit the manuals to their installation CD. This is the only dcument I found online showing a possible connection of a Siemsen S7-300 with a PMU-330BTE, and it is sketchy. Therre is nothing describing an MPI cable for the programmig port of the S7-300, using the RS-485 communicarui port of the panel (using the RS-232 port would require an MPI adapter cable:or RS-232 to RS 485 converter of some kind, not described). https://manualzz.com/doc/7083955/hmi-pmu-series-eng You must either refer to the installation CD that accompanies this panel, or contact LG-IS directly to find that nformation, and also on the creation of tags for their S7-300 driver, so that you can exchange data with the S7-300 CPU.. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 06/13/2021 01:48:17Last edited by: dchartier at: 06/13/2021 01:51:00 |
|
This contribution was helpful to1 thankful Users |