hi, 3-wire-transducers are like 4-wire-transducers with a combined M. so Measuring range module should be set to C. Wiring is described here: Analog input module SM 331; AI 8 x 12 bit;(6ES7331-7KF02-0AB0) 24VDC of the sensor is clear. The one wire for measuring goes on "+" of the chanel and the "-" of the chanel goes to M of the same potential of the power-supply of the sensor. hope this helps, regards, |