1/20/2022 11:34 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hi Barra1, the parameter @4r%.2f@ in a message says, that you use the associated values 4 of the message. If you look at the APL manual you can see that the associated values 4 is connected with the input ExtVa104 (for more information see the manuals PCS 7 Advanced Process Library (V8.1) at section MonAnL messaging and SIMATIC Programming with STEP 7 at section "Adding Associated Values to Messages"). But as you can see in the manual PCS 7 Advanced Process Library (V8.1) at section MonAnL messaging there is not the PV_AL_Lim as associated values. And it is not possibility to connect an input with an input. With regards |