I have a Step5 PLC, CPU155U, 948 connected to 4 RTUs (ET200M). The CPU goes to stop and one of the ET200M stations gives BF. The ISTACK is attched, but I'm no expert in Step5. How can I trace the problem? AttachmentDesktop.zip (203 Downloads) |
The more you know, The more you know that you don't know |
|
4/27/2016 4:41 PM | |
Joined: 9/7/2007 Last visit: 8/30/2023 Posts: 550 Rating: (62) |
Hi AMAZINGAHMED You can find attached related parameterizing for DB1
AttachmentError in DB1.pdf (316 Downloads) |
Best Regards |
|
4/27/2016 4:49 PM | |
Joined: 7/18/2011 Last visit: 10/9/2023 Posts: 521 Rating: (91) |
This is information for S5-115U. The problem is in CPU 155U |
4/27/2016 5:05 PM | |
Posts: 8946 Rating: (999) |
This nanual is for 115U but NOT for 150/155U. |
4/28/2016 4:01 AM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308)
|
Hello What I can understand from ISTACK is : DI Module containing Inout Byte 35 is listed in Input list of DB1 , however the CPU is not able to detect it on Startup. Pl check the module / connection to the rack containing this module. For more details pl download and read the Manual : S5-155U CPU 948 Programming Guide Check out Chapter-5 - Interrupt and Error Diagnostics Hope this helps Cheers Navnag |
Last edited by: Navnag at: 4/28/2016 4:02:50 AMThere is no such thing as the last bug in a program |
|
4/28/2016 11:09 AM | |
Joined: 9/7/2007 Last visit: 8/30/2023 Posts: 550 Rating: (62) |
Excuse me For this mistake, Here is the related manual: SIMATIC S5 Programming Guide S5-155U CPU 948 This may help
AttachmentCPU948.pdf (268 Downloads) |