7/28/2017 6:45 PM | |
Joined: 9/27/2006 Last visit: 9/25/2024 Posts: 12283 Rating: (2685) |
Hello; It seems the FUMs are Function Modules used to couple a S7-400H AS with remote I/Os over Profibus (at least that seems correct for the IM616) for SPPA-T2000 systems. They seem to serve the same purpose than the S5 IM 314, for remote racks, See the description in the following document: https://www.siemens.com.tr/i/content/3851_1_AS%20620B%20HW-exchange%20S5%20to%20S7_e.pdf Kargan, the answer to your question could be delicate, since most of us ere are unaware of Power Generation controllers such as SPPA-T2000. But if my (albeit limited) experience of PCS 7 used in our projects, the tags collected through Profibus-DP should be available through connection with the redundant AS-masters, and therefore directly accessible to the PCS 7 controllers. Do you have any support link you can ask for your specialized control system? If you search for SPPA-Tx000 on this site, you will find a very few number of request for help, and fewer answers from our side... Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 7/28/2017 9:40:48 PM |
|